IMO only if the board is totally isolated. and even then, treat it as a live conductor.
 
IMO, if the entire installation is safely isolated and all electronice equipment is disconnected (I'm thinking emergency lighting here) there should not be any current flow in any of the line conductors ergo there shouldn't be any return current flow in the neutral conductor.

For safety's sake I would terminate the supply neutral tail into a connector block of some description for the duaration of the test just as an added precaution.
 
I use one of those all plastic spring clamps, I can get the bared copper completly enclosed, I was just wondering what the "offiical" line was and GN3 says nowt about it, I might run it past my NICEIC area rep although it will probably be a case of what we in Scotland call "skelfs in the erse" from sitting on the fence
Pict
 
You are always going to get a 'dead short' reading if it is TNC-S (PME) any how. Years ago when I worked for hydroboard it was common practice to fit a swivel link on the neutral along with the earth. We were always taught to carryout IR on circuits before final connections to DB's
 
The neutral has to be disconnected to do the N-E IR test. Personally I would disconnect and immediately do the N-E test and then reconnect the neutral.

The reason for my method, if there are downstream single phase circuits and you forget to reconnect the neutral. And then close the 3 phase switch you will put 400v across the single phase loads. And you would not be very popular if you did that.
 
Many Many years ago I was fitting a single pole MCB to a three phase board which was in a cupboard full of junk I knelt on a table leaned across some boxes and fitted the breaker, but caught two prongs of different phases, jeez what a bang, I took out the isolator and vapourised the copper prongs, just because they did not want the power of during lunches, I learnt a two valuable lessons one I am not immortal and two safe isolation is done for a reason. So Oxo your right, your only popular if no one knows you even in the building.
Pict
 

Reply to IR on a whole board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
961
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
711
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top