Hi all, l recently did a eicr on a fish and chip shop.

3 phases (only one phase in use by chip shop). Earth conductor is welded together to each phase by TN-S earthing system means.

When it came to the IR test, l tested the norm tests, L-E, L-N & N-E.

Bearing in mind that we are now supposed to do the IR test without disconnecting the conductors from the CU.

All L-E readings were ok (in the hundreds Mohms).
All L-N readings were ok (same)
All of my IR tests between N-E are exactly the same on the Wylex, due to the fact that the only place l can test TO (without disconnecting conductors) is between the Neutral busbar and the earth bar.

All readings on every circuit were 0.71Mohms, which is obviously far too low.

Can l just ask where im going wrong? I normally disconnect the conductors for an accurate reading but have been told not to by other sparkys, due to regs (which im unsure of the reg this covers).

Any advice or feedback anyone???


:uhoh2::uhoh2::uhoh2::uhoh2:
 
On a periodic, you only need to test between L&N to E.

I've probably misinterpreted your post, remember, N & E are essentially connected, so N to E would be zero.
 
Whoever is telling you that your not to disconnect conductors needs a kick up the arse.

Yes you "may" do a global test across bus bars and neutral bars etc etc... But ONLY as a time saver..!
ie if you do those three tests at the CU and all is well, then job done..!! (As far as IR testing is concerned.. )

However nothing precludes you testing individual circuits. It's a very occurrence that a global IR test comes good at first bite. They nearly always need splitting down further to see where the problem child is. !

Have you read this mysterious "reg"..??
 
  • Like
Reactions: 1 person
where did you read that on a pir you only need to test between L&N to E ? i am not saying its untrue but i have never read this
 
GN3.

Periodics, you're just testing the install is safe, ie, no Exposed parts can be live.
A L to N fault would just result in a short circuit and the breaker would trip.
 
The recommendations are not to disconnect the cpc (in case you forget to reconnect it) when carrying out IR tests now, nothing to do with neutrals.
 
which is silly if you think about it. if you forget to reconnect a N in the CU, then 1. that circuit will not work. 2. all the circuit cables ( except cpc) would be live. same reason that fuses in the neutral line were scrapped years ago.
 
Thanks to everyone that replied.

No Archy, l never read the reg. Its merely sparky talk between friends.

I must have mis-understood the people who have told me this or they have it wrong.

Thank you all. All feedback duly noted..
 
I think it was changed in 2008 - Reg 612-3-1
 
A global test ie Ln to earth tells me it's ok if readings are good to change old rewritable DBS to new 17th edition ones just done one yesterday
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ir test on bs 3036 wylex board
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
Jabbajaws,
Last reply from
Farmelectrics,
Replies
10
Views
2,080

Advert