Discuss IR Testing; what is the correct procedure? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Goody

-
Reaction score
94
Whilst testing Insulation Resistance between L & N, L&E and N&E (radial or a ring circuit); I know the L and N should be disconnected from the bars but should the earth be left in on the earth bar on the DB or should be removed? I had been doing IR only by disconnecting all the three from the bar until now:mickey:. Many thanks!
 
i prefer to dis all 3 ( 6 on a rfc.) then there's no possibility of parallel paths giving a false reading.
 
Better practice at the early stages to remove all conductors so you are in full control (or so you assume) of the installation under test.
 

Reply to IR Testing; what is the correct procedure? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
380
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
728
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
799
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock