Discuss IR Testing in the Australia area at ElectriciansForums.net

Reaction score
32
Hi,
When IR testing a circuit where voltage sensitive devices cannot be easily removed, and using test method 2 as per GN3, where they advise connecting line & neutral together and then testing to earth from this connection. Is there any reason not to just test between line & earth and then from neutral to earth ?
I,m probably missing something as usual but can,t see the reason for joining line & neutral together.
Thanks.
 
you join L and E to avoid any possibility of applying the test voltage across a sensitive load. as they are shorted, they are at the same potential.
 
You can test at a reduced test voltage ie. 250V DC so as not to activate the voltage dependant resistor of the surge protection device. (1 MOhm still applies)

You join L+N together to prevent a potential difference across sensitive devices such as passive sensors and control gear etc.
 

Reply to IR Testing in the Australia area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
587
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
319
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock