Discuss Is 2way switching for a fan the same wiring as 2 way lighting?? in the UK Electrical Forum area at ElectriciansForums.net
J
J_c9sh
hi, doing some work for client and they have asked for a fan to be 2 way switched, 1 switch in utility room and the other in the bathroom next door
my query - is 2 way switching for a fan the same wiring as 2 way lighting with a permanent feed going to the fan for a run on timer??
thanks
I'd go for 2 separate fans as well - one in the bathroom, one in the utility room. Then you could have the fans coming on with the lights, like 'normal'.
Otherwise the lights would all come on together unless you start messing about with diodes and relays and that, by which time you might as well have installed 2 fans anyway.
i would put the 3p isolator before the fan of course lol but would you use strappers , s/w, pernament feed etc like 2 way lighting
just need to know correct wiring
thanks
this is what they want
utility room - 1 2g switch, one for light and one for fan
bathroom - 1 2g switch, one for light and one for fan but 2 wayed with utility room switch
lights on seperate switch
I honestly think it'll be cheaper, quicker and a lot less hassle with two extract fans. In the long term I'd say the customer will thank you for it
i never installed 2 way fan control before,i have always installed 2 seperate fans as you mentioned trev but if in future i was to do it is wiring same as lighting - im going to talk to client about changing to 2 seperate fans, makes more sense
Light = item of electrical equipment.
Fan = item of electrical equipment.
Both require N and switched L and one requires and permanent L.
No reason why you can't 2 way switch, EXCEPT,
Upon loss of switched Live, you can see one has gone off, but the other one goes into timed off mode.
Unless you fit an indicator at each switch, you'll never be sure the fan is going to go off.
if you're not using the lighting switching to activate the fan, then it's a simple 2 way switching arrangement to activate the fan. a permanent L to the fan if you want overrun. isolator is optional if there's natural light available for maintenance purposes.
Firstly i would check the required ventilation rates for these two rooms as they will be different if you check the book, also they are ducted together so I guess this must be an in-line fan so someone can invertently turn it off if required in the other room.
All sounds alot of agro with no real gain. The same amount of wiring and the same amount of ducting. Only thing being saved is the cost of a fan unit. If I came across this setup I would assume DIY.
only way i can see it working as you want it to is to drop a perm feed to fan and bring 2x switch cables off from the isolator to the switches...!
that way you would need to turn the switches off after use in that room.
Reply to Is 2way switching for a fan the same wiring as 2 way lighting?? in the UK Electrical Forum area at ElectriciansForums.net
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
