Hi all, probably being really thick so apologies if I am!
Just wondered why led strip comes with such a thin supply cable?
For eg 10m x 9.6w = 96w \ 12v = 8 A.
So ideally not accounting for volt drop etc a minimum of 1.0mm csa needed.
Why does most led strip come with a supply cable of maximum of 0.5mm ( maybe even less)
I know most lengths of this size come in 24v, just using 12v as example.
Thanks again.
 
there's no way LED strips draw that much current. wheere did you get 9.6watts from?
 
there's no way LED strips draw that much current. wheere did you get 9.6watts from?

I have fitted many LEDs ranging from about 4w to 14w a metre (5v,12v,24v), it really depends on how many LEDs per metre there are, eg: 10,20,30,60 per metre

Also colour makes a huge difference and whether they are RGB(W)(A)
eg: a normal 20ma LED in RGB is 60ma because there are 3 colours but that 60ma is a MAX and assumes you have it on white full brightness (R=255,G=255,B=255)

@OP Do you realise you should feed 10m from both ends?

Depending on the voltage and brand of the LED, it should be fed from approx every 5m otherwise you will see the LED getting noticeably dimmer due to voltage drop and also so the load is shared similar to a RFC
 
Thanks Hex Hex. Suppliers not mentioning any names say anything up to 10m is fine on one strip and vd wouldn’t cause dimming, however in the past like you said I normally split so have 2 lots of 5m.
I have never heard of having it like an rfc though. Do you just double the ends up in the driver?
I have also heard people say they just use the correct sized speaker wire to supply it, but always used 2 core flex myself.
 
I have never heard of having it like an rfc though. Do you just double the ends up in the driver?

I don't mean actually wire it like a RFC but feed both ends or every 5m, so the load is shared like a RFC

if its 1 x 10m length then I would run a flex from end to start and connect your feed to both at the start or yes you could run 2 from the driver, it really depends where the driver is
 

Reply to LED Strip lighting supply cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First time poster here seeking a little advice/confirmation I have spurred off to a fused switch and from there running two 2.5mm cables to the...
Replies
2
Views
714
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
748
Hello, We moved into our house 2 years ago and until recently the kitchen lights worked fine. The LED strip lights are on a dimmer switch, when...
Replies
4
Views
2K
Hello all. I want to fit LED strip lights to the ceiling with 45 degree channeling and diffuser around my son’s room. As there are so many...
Replies
3
Views
1K
Hi - sorry if this has been posted elsewhere but i cant seem to find the answer. I have an LED Strip and a smart controller. I need a power...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock