Discuss Live Testing - PEFC / PSCC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A
adam1984
After a little bit of advice please
We are doing our Dead and Live Testing at college tonight. I am ok on most of it but due to not having much time to practice our live testing I need a bt of advice.
Live Test:
CCU breaker off
Prove VID - Test for dead with VID - Re-prove
Ze - remove main earthing cable - test between earth and live on incoming supply? (reconnect earth straight after)
RCD - we have a plug for that test and i am happy with the seven test we do for that.
Now the bit I am stuck on is the PFC / PSCC. I know the test (PFC Live / Earth- PSCC Live / Neutral) but do I have the breaker on or off?
Any help much appreciated and also if I have missed anything off.
Not sure how your college wants you do do the PFC tests, but I would always do them straight after the Ze test, reconnect the earth with the main switch open, installation off, test.
I'm sure that is how the college will want it done, because the CD/DB is dead apart from the switch, so less likely of you coming into contacts with live parts
Thats the way I would do it too, not teaching you to suck eggs but don't forget to record the highest reading. And don't leave the cover off unattended.
GN 3 is your friend
look at the sequence of tests and this will indicate to you what state your DB would be in at the point of testing PSCC if you follow that how can you be wrong!
if single phase he will only have 1 result if 3 phase he needs to take the highest reading and double it!
Thanks for the responses guys. It will be a single phase installation. So if i have interprted the replies correct it will be the Main incoming swith on with the CCU breaker in the off posistion?
For my Ze I will test at the incoming live. PFC at the incoming side of the CCU breaker?
Unfortunately i have not got the regs book only my OSG and Amicus book.
not CCU breaker..... CCU Main Switch OFF and measure on incoming ( live ) terminals L/N and L/E.
Reply to Live Testing - PEFC / PSCC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Hi guys I'm looking for some advice. I have recently removed a wall socket that we no longer need, and have wrapped the individual Live, Earth and...
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...