Discuss Low Insulation resistance test on smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
King84
Trainee
Hi Everyone
Just a question bothering me as you cannot do Insulation resistance test on smoke detectors as they can become damaged so obviously smoke detectors are sensitive but they are also installed on lighting circuit so if perform low insulation resistance test 250V between Live and earth would that be safe or still they should be disconnected first or if not possible then it is a limitation ?
SOme of these are badly fitted and I sometime avoid taking them down incase if they dont fit back properly so was wondering if I could test with low IR by using Line,Neture together with earth
You can test at 250VDC but the internal circuitry of the heads will probably give you poor readings.
Best to do line/neutral to earth, I tend to do 250VDC first in case of current using equipment still fitted that might throw your results such as switched mode power supplies, the 500VDC if I'm happy to proceed.
I'm guessing this is for periodic inspection rather than new installation?
If they’re badly fitted I’d still want to take them down before testing, then code accordingly and rectify where needed.
Reply to Low Insulation resistance test on smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...