Just done a quick test on a ring for a friend, the results are as follows.
Continuity tests are all fine.

Insulation Resistance:
Line - Neutral = >299 MΩ
Line - CPC = >299 MΩ
Neutral - CPC 39.6 MΩ

Where should I begin in finding the problem with the N-E low IR.:confused:

Thank you.
 
Yes disconected at board.
Removed both legs of ring at board and tested L- E, L-N, N-E.

quick responses thank you guys.
 
Last edited by a moderator:
here are the continuity results:

r1 = 0.44
r2 = 1.35
rn = 0.55

(R1+R2) at all socket outlets were between 0.38 (min) to 0.46(max)


Thanks
 
you say its ok but r1 and rn have different readings its a ring so they should be the same r2 should be higher (assuming 2.5 t&e installation) due to higher resistance, code 3 im afraid further investigation required
 
yup just realised that r1 and rn are 0.1Ω difference and as far as I can remember isnt the maximum supposed to be a difference of only 0.05Ω
Yup further investigation required.

What could be a cause of this, a screw catching the neutral someplace?
 
could be mice chewing on cables for all i know (sorry but with out seeing it pretty hard from where im sat to say thats yours problem)
but what i would check first is all appliances un plugged, neons turned off, isolated all spurs (test later if needed) etc then re test. if that dont work split ring (think of it as two radials) and re test. in theory one radial will be faulty one will be ok. keep splitting 'faulty radial' till you find the 1. previously un noticed fuse spur with neon and dodgy connections! or 2. bad leg of cable that the mice have been eating!!!!!!
have fun!
 

Reply to low IR N-E in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
902
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
670
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
764
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
690
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock