Yes there is Boff, it seems to me there is a failure to communicate, so tell me Boff what or where does the 0.05ohm come from and what is it related to?
 
That is spot on, hit the nail on the head
Sadly..no.

This thread had potential to shed some light on a poorly understood issue that a lot of people(including me) an take a lot from. I thought that my post (although I cannot take full credit from it, as I said, I had to 'phone a friend) gave all the explanation neded.

I will reiterate for clarity.

The 0.05 value is the value below which potential difference should be, between simultaneously accessible extraneous conductive parts. Example of which is a gas pipe and a water pipe next to each other. Test between the two.

Even if both are 10mm bonded individually back to MET, if the difference between the two is greater than 0.05 then they need to be bonded to each other.

The 0.05 figure is not a value to be achieved between MET and bonding point taking into account the value of resistance of the cable.

That is how I understand it, of course, I am open to other more enlightened people's wisdom.

Regards.
 
Never, I will never grow up and you can't make me Boff, so there ya cheeky little monkey…as an aside I wonder what that 0.05 ohms might mean?
 
Boff, you may not understand this, but there are sticks and some of them are for throwing but unfortunately Boff these sticks are not stones and will not break my bones.
 
New posts

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
795
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi I have a 1st fix domestic install on the go and need to leave a socket for other trades to use after me. There is no main bonding at the...
Replies
7
Views
859
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
418
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock