If I change a main db that supplies multiple sub-dis boards, how extensive do I test? Can I just test the main db and supply cables to existing sub boards? Or do I have to test all the outgoing circuits of sub db too? I would complete a full eicr before.

theoretical question btw.
 
I would only test the circuits from the board you have changed, not the circuits from the boards they feed.....if that makes sense?? i.e if you change a db in a house and that db feeds a garage db aswell, you would only test the circuit feeding the garage db, not the garage installation.
 
Last edited:
I would of thought you only have to test what you change and do a quick functional test on what it feeds should suffice? Or check c.p.c if worried.
 
You only need to carry out tests on supply circuits leaving the board you are going to change and also verify correct earthing and bonding and main supply parameters. Make a note on your EIC of the extent of works and testing completed (this will cover you)
 
well if i carried out a full periodic prior to the db change i wouldnt do any further tests after other than Zs measurement at each db.
pointless unless you enjoying doing it all twice.
;-)
 
You would only be responsible for the circuits you worked on, this doesn't include final circuits supplied from the distribution circuits you altered. Even if you were to find some C2ish defects
you could still re-connect and list it in departures, you're still making the place safer.
 

Reply to Main db change in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
540
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
506
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock