Apologies if this question sounds a bit basic but am a little confused at the mo and quite new to the game. Here goes -

I am trying to complete a NICEIC Highway Installation Certificate for a system where there is a 230 v TT supply coming into a roadside pillar into the main BS88 fused head. 6mm Meter tails then take this into a 30mA RCBO which protects the sole circuit to an accessory.

So on the certificate I have 2 circuits - 1. Supply (Distribution) and 2. Final circuit to accessory (Final)

I know there is some debate on using the 1667 ohm / 200 ohm as max Zs for the protected final circuit figure but what should I use for the max Zs of the actual supply / distribution circuit ?

If i was working on a TN system I could happily just look up the max Zs figures using Table 41.2 but am a bit stumped with this TT scenario.

Any help on this welcomed. Thanks
 
thanks i=p/u - do you think its okay to put this even though its not an rcd protected final cicuit?
 
sorry reading this wrong, whatever fuse is protecting the dis circuit will have a value
 
A C6 BS61009-1 RCBO protects the final circuit so max Zs (from table 41.5) I can take as 1667 ohms.

but its the gG16 BS88 supply/distribution circuit that I am trying to find the max Zs value for.
 
Maximum Values of Loop Impedance (Zs) for comparison with test readings based on 80% of maximum values above (as per Appendix 14)
Rating of Protective Device
Protective device
(MCB/ Fuse)
Disconnection
time (s)
5A
6A
10
15A
16A
20A
25A
30A
32A
40A
45A
50A
60A
63A
80A
100A
BS EN 60898 Type B
0.4 & 5
7.36
6.14
3.68
2.46
2.30
1.84
1.47
1.28
1.15
0.92
0.82
0.74
0.58
0.46
0.37
BS EN 60898 Type C
0.4 & 5
3.06
1.84
1.15
0.92
0.74
0.58
0.46
0.37
0.29
0.23
0.18
BS EN 60898 Type D
0.4 & 5
1.54
0.92
0.58
0.46
0.37
0.29
0.23
0.18
0.14
0.11
0.09
0.4
8.36
2.62
1.36
0.92
0.48
BS 1361
Cartridge Fuse
5
13.12
4.00
2.24
0.77
1.47
0.56
0.77
0.56
0.40
0.29
0.4
6.82
4.09
2.16
1.42
1.15
0.83
0.66
0.48
BS 88
HBC fuse
5
10.8
5.94
3.34
2.33
1.84
1.47
1.08
0.83
0.66
0.46
0.34
 
3.34ohms is the 80% value .. sorry my copy and paste didnt come out right
 
  • Like
Reactions: 1 person
should i be using simple ohms law then? so for example if it is a 16A fuse then 230v/16a = 14 ohms? my max Zs would be 14 ohms?

- - - Updated - - -

sorry i posted my last whilst you posted that last message
 
3 times 16 =48 , 230 /48 = 4.7 x 0.8 =3.8

but all type b breakers is 5 times, c = 10 times, d=20 times

- - - Updated - - -

you got the green book? big 1
 
sorry but why are you multiplying the fuse rating by 3?

I only have the big red book at the mo - green one on order
 
3 times the rated current of fuse it takes to blow instantly, then is why if your zs is over this it wont blow instantly in a fault...
 
thanks a lot for your help i=p/u. i will try and bounce a few thoughts off some of the guys from work on this one also.
 
it makes sense eventually... im only on year four but have done 2391 over ten weeks at a college which i think made it stick for me.... and never ending querstions..
 
i understand your formula but whereabouts can i find the "3 times rated current" in the regs do you know?
 
You have a distribution circuit protected by a 16A BS88 fuse on a TT system so your disconnection time is one second.
The time current characteristic tables in APP3 of BGB (p300) show a table in the top right for disconnection currents for various times.
From the table a BS88-2 16A with 1s Disconnection time has a minimum current required to trip of 75A.
230V / 75A = 3.1 ohms
So max Zs of dist circuit is 3.1 ohms at 70ºC
(In BRB p248 and 72A)
 
  • Like
Reactions: 2 people
he needs a book , i use me braIN LOL
 
another silly question of the day why 1 second disconection time? because street lighting?
 
I know all this stuff, but it aint easy remembering it all..... Someday aaa.
 
  • Like
Reactions: 1 person
Thanks for your responses - the second part of Richard Burn's response has really hit the bullseye.
Thanks again for all the contributions!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Max Zs value for TT distribution circuit (NOT Final circuit!)
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
zak325,
Last reply from
zak325,
Replies
20
Views
4,172

Advert