Hi guys,

We were testing an install the other day with a new meter megger 1553.
Ze is a LIM as we cannot disconnect earthing
Could not test IR on this circuit due to electronics connected.
Did long lead R2 but it's all conduit with no separate CPC and no fly leads at accessories but has plastic fittings. Then tried Zs but it comes up on display as "Trip" and does not give a reading but does not actually trip the 10A 3871 type 3 breaker
Went and got old Fluke 1652 from van but it's out of calibration and tried it with that using the 3 leads but still no joy.
I assume it will not give a reading as a safety measure as the touch voltage may rise too high due to poor insulation resistance? But this is just a guess. I can't find any documentation on this.
I have now emailed Megger but they have not got back to me. I just thought someone on here might know. Cheers
 
Hi guys,

We were testing an install the other day with a new meter megger 1553.
Ze is a LIM as we cannot disconnect earthing
Ze cannot be a "LIM" you obtain by enquiry.
Could not test IR on this circuit due to electronics connected.
Could you not have measured L&N together to E???
Did long lead R2 but it's all conduit with no separate CPC and no fly leads at accessories but has plastic fittings. Then tried Zs but it comes up on display as "Trip" and does not give a reading but does not actually trip the 10A 3871 type 3 breaker This is because as you've said the meter cut out on the test as the touch voltage rises above the safe threshold.
Went and got old Fluke 1652 from van but it's out of calibration and tried it with that using the 3 leads but still no joy.
I assume it will not give a reading as a safety measure as the touch voltage may rise too high due to poor insulation resistance? But this is just a guess. I can't find any documentation on this.
I have now emailed Megger but they have not got back to me. I just thought someone on here might know. Cheers


I'm confused, you say you did an install, was this a new install or just additions and alterations to existing???

I'll reserve judgement until you clarify your situation a bit.
 
Lenny

Sorry I should have said it was a PIR.
And I've found out now what the problem is.
There are 3 single phase isolators in the switchroom/plantroom (well loads more really but these are the ones affecting it) and you need to disconnect all 3 to Isolate any one phase.
So there's a voltage of about 120v on this circuit when isolated, therefore the meter won't allow a test. It's just the "Trip" message I was unfamiliar with on this meter and could not find reference to it in the manual (still can't).

Also can't do IR - L+N to earth without disconnecting the earth(s) (not possible) and an ELV safety circuit has also been connected to this circuit - not good!

Thanks anyway
 
Hi guys,

We were testing an install the other day with a new meter megger 1553.
Ze is a LIM as we cannot disconnect earthing
Could not test IR on this circuit due to electronics connected.
Did long lead R2 but it's all conduit with no separate CPC and no fly leads at accessories but has plastic fittings. Then tried Zs but it comes up on display as "Trip" and does not give a reading but does not actually trip the 10A 3871 type 3 breaker
Went and got old Fluke 1652 from van but it's out of calibration and tried it with that using the 3 leads but still no joy.
I assume it will not give a reading as a safety measure as the touch voltage may rise too high due to poor insulation resistance? But this is just a guess. I can't find any documentation on this.
I have now emailed Megger but they have not got back to me. I just thought someone on here might know. Cheers

When you did your Zs were you using the mains lead or fly leads ?

The usual error that causes the trp display is
.Measuruing Zs on low current setting without the third lead ( black goes in no trip at top) test at fitting black on neutral green on earth etc, these must be secure connections , any movement during the test will cause the to display trp
 

Reply to megger 1553 multi functional tester in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
598
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Megger 1553 multifunctional tester complete with fittings and leads also calibration certificate included comes complete with case and various...
Replies
0
Views
942
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock