Discuss Meter tails and capping in the UK Electrical Forum area at ElectriciansForums.net
magnoliafan89
Hi guys came across meter tails buried less than 50mm no rcd protection but did have some red capping over and they are in prescribed zone about a meter between main fuse and consumer unit.
TNS system.
C2 or no code??
Depends what the red capping is. If it affords protection to comply with 522.6.204 (iv) then no code.
I would usually apply C3 to cables buried less than 50mm with no RCD for additional protection.
definitely requires a code.C3 or even a C2 if you think some numpty might nail or screw.
A section that resists penetration (3mm steel is usually considered adequate) does not have to be earthed for that reg. Normal capping would not be suitable.
If using something else i think it has the be conduit or trunking to BS standards and earthed.
Years ago as an apprentice, we put tails into 20mm steel conduit when buried in the plaster. So 3 tracks and 3 pipes. Boards where below the staircase, dunno why my boss never asked the builders for the pirmelli box to be located level with the area the Fusebox was installed.
Reply to Meter tails and capping in the UK Electrical Forum area at ElectriciansForums.net
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away...
5K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
4K