Anyone had any experience of metrel testers tripping an RCD when doing a Zs when you have the rcd no trip function on?

It happened the other day on my 2391 assessment but the college tester did the same so I assumed it was the college rig.

Just wired up a cooker for my niece, can't do a Zs. Tested the rcd and that's fine.

Pain in the rear.
 
Uumm. I'll another look tomorrow.
 
Is the RCD part of a split load arrangement? It sometimes happens that existing and test earth currents add together to trip the RCD or RCBO, especially if the RCD is on the sensitive side. Have you ramp tested the RCD to see if it is on the sensitive side?
 
Last edited:
It's an RCBO. No load on the circuit
 
The RCBO might be on the sensitive side so worth ramp testing it to confirm that isn't a factor. It's also worth checking the tester on other circuits to see if it causes the issue with any RCD/RCBO as there is always the possiblity that it could be the problem or at least twards the extreme end of spec so will cause a trip most of the time.

You could always by pass the RCBO for the test by temporarly swapping it out for and MCB.
 
I ramp tested it. 22ms.
 
You need to change the meter settings so that it gives you the tripping current in mA as opposed to time (my old Metrel Eurotest XE has a ramp test option that allows for this). Most no testers no trip loop test will use a current of around 15mA so if the RCD is sensitive or your tester is for some reason pushing a current higher than 15mA then you are likely to end up with a trip.
 
  • Like
Reactions: static zap
Sorry sparkiemarky, it was meant to be 25ma not Ms.
 
Anyone had any experience of metrel testers tripping an RCD when doing a Zs when you have the rcd no trip function on?

It happened the other day on my 2391 assessment but the college tester did the same so I assumed it was the college rig.

Just wired up a cooker for my niece, can't do a Zs. Tested the rcd and that's fine.

Pain in the rear.
Are you using the three leads when taking the Zs?
 
 
Tel, absolutely haha

Bad day. Won't do that again.
 
  • Agree
Reactions: timbobelfast
download.jpg
 
Oh well at least you know there isn’t a problem with your tester :tearsofjoy:
 
Ha ha, I should never have read this thread. Today was downlight day. After 15 it feels like Groundhog Day but I still got the sore back, sore neck you name it. Anyway, part way through I'm up a ladder on the last downlight in a string. So I'm thinking now's the time for a "no trip Zs". Bleeping thing tripped the RCBO ... Swear I've never had that before. Re-set RCBO and no problem, trip - what trip? Jinxed I say, jinxed !!!
 
  • Funny
Reactions: gazdkw82
Ha ha, I should never have read this thread. Today was downlight day. After 15 it feels like Groundhog Day but I still got the sore back, sore neck you name it. Anyway, part way through I'm up a ladder on the last downlight in a string. So I'm thinking now's the time for a "no trip Zs". Bleeping thing tripped the RCBO ... Swear I've never had that before. Re-set RCBO and no problem, trip - what trip? Jinxed I say, jinxed !!!
bet your sausage fingers shorted something out the 1st time.

and 15 downlights? what did you do after morning coffee break?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
~
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Metrel MI3000 Zs(rcd) tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
gazdkw82,
Last reply from
buzzlightyear,
Replies
18
Views
4,366

Advert