cagedanimal2010

evening all,

Doing an EICR on a small place, TT, only problem i'v found so far, is the stake has been cemented over(garden has been all done), Ze is 122.07 Ohms. agree reading is fine however cannot verify final connection.Could this be classified as c1? what code would you guys give it, i would like to "push for" the replace rod and pull in new earth.

Many thanks!!!
Danny
 
Last edited by a moderator:
Its not about us, its your opinion that you have to justify.
You do have a reading that could do with improving, if you pull on the cable any where is it taught or loose?

C3.

But make it clear that you can not inspect it and that it should be accessible.
 
Last edited by a moderator:
im asking for opinions that is all. not loose anywhere.
dont want to seem ott, however it is the main earth.
 
Last edited by a moderator:
I would code as C3 as there is no chance of danger of the earth becoming loose! However there is also no chance of ensuring it is currently secure or appropriately labelled, so it would require further investigation.
Recommendation that the earth rod connection be accessible for maintenance.
 
'If any observation in the report has been given a Code C1 or Code C2 classification............, or if any observations require further investigation to determine whether danger or potential danger exists, the overall assessment of the condition of the installation must be reported to be‘unsatisfactory’. '

(extract from ESC best practice guide 4-2011 as at 10/01/12)


As this extract states, any further investigation reported should class the installation as unsatisfactory.

Use your own judgement as to what danger is, or could be present and code accordingly.
 
Last edited by a moderator:

Reply to More EICR. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
800
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi all, just looking for guidance on how you would code a 2.5mm main earthing conductor on a property with 10mm line conductor. Basically on a...
Replies
2
Views
2K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock