Discuss more questions on test certificates in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

pageboy

ive installed a new shower circuit, so i do a full sequence of tests for the new circuit and put them on a electrical installation certificate.........


Q1. do i fill in the inspection sheets as i would if it was an initial verification, also completing the particulars at the origin,and also doing all ze, pfc tests, continuity of main bonding conductors ect....

Q2. the consumer unit has a 100a main switch, a 63a main rcd and another 63a rcd, the shower is on a 50a breaker, so do i need to carry out an rcd test on the shower even tho its not directly connected to an rcd:confused:
any advice muchos gracias

more questions may follow!!!!
 
an electrical installation certificate is required for a new installation, an addition, or an alteration. as your installation work constitues an addition it clearly needs a full electrical installation certificate.
 
with regard to your shower, it MUST have an rcd or rcbo giving additional protection. the rcd already fitted has only got to be tested on any one circuit as the results will apply equally to all the circuits protectd by the rcd
 
ive installed a new shower circuit, so i do a full sequence of tests for the new circuit and put them on a electrical installation certificate.........


Q1. do i fill in the inspection sheets as i would if it was an initial verification, also completing the particulars at the origin,and also doing all ze, pfc tests, continuity of main bonding conductors ect....Yes.

Q2. the consumer unit has a 100a main switch, a 63a main rcd and another 63a rcd, the shower is on a 50a breaker, so do i need to carry out an rcd test on the shower even tho its not directly connected to an rcd:confused: Sounds like a dual RCD CU you have there, so the shower MCB will be protected by one of these RCD's (if not then it should be!!)
any advice muchos gracias

more questions may follow!!!!

GN3 has guidance on insp and testing, what is needed and when etc.
 

Reply to more questions on test certificates in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
839
Hello, I am in the process of training to be an electrician and have a question. When filling out a EIC for a new circuit am I required to test...
Replies
2
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
703

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock