Wiring RF thermostat receivers to valiant boilers...

We have been using standard 0.75mm 5 Core flex, from the receiver to the boiler (reference method B). Obviously the flex is carrying L-N-E at 230v and also two switch wires ‘boiler on’ ‘boiler off’ at 24v. However someone has made a comment on carrying band 1 and band 2 in the same cable, saying it’s not allowed. All conductors are insulated to 230v and the regs are like blurred lines.

Can anyone offer any advice?

Thanks
 
Not sure about 1 & 2 in the same cable, but I think you could cause problems with induced voltages on the extra low voltage cables.
 
Wiring RF thermostat receivers to valiant boilers...

We have been using standard 0.75mm 5 Core flex, from the receiver to the boiler (reference method B). Obviously the flex is carrying L-N-E at 230v and also two switch wires ‘boiler on’ ‘boiler off’ at 24v. However someone has made a comment on carrying band 1 and band 2 in the same cable, saying it’s not allowed. All conductors are insulated to 230v and the regs are like blurred lines.

Can anyone offer any advice?

Thanks

Your setup complies with reg 528.1 (ii), so it is allowed.
As above, Induced voltage may be a problem.

upload_2019-2-13_7-25-29.png
 
No issues as long as the insulation of the conductors is rated at or greater than the maximum voltage it will be used with.

Induced voltage shouldn't be an issue here, as the 24V can be seen as a digital signal, either on or off. This depends on the impedance of the input to switch the boiler. Does it trigger a relay or is it to an input on a circuit board?
 
  • Like
  • Agree
Reactions: DPG and rapparee
No issues as long as the insulation of the conductors is rated at or greater than the maximum voltage it will be used with.

Induced voltage shouldn't be an issue here, as the 24V can be seen as a digital signal, either on or off. This depends on the impedance of the input to switch the boiler. Does it trigger a relay or is it to an input on a circuit board?
The connection is a 24v RT terminal on the boiler circuit board. The Switching is done within the receiver.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Multicore cable voltages
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
Ash4189,
Last reply from
Ash4189,
Replies
4
Views
4,254

Advert