Discuss New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net

Ok this is all very well and could go on for weeks but please quote the exact wording of the exact regulation that clearly states armour must be earthed at the supply end.

Edit - reply to post #57.
 
Last edited:
Does this statement suggest that it can be connected to whatever earthing arrangement exists at the origin OR alternatively, connected to a separate earthing arrangement at the load end?
It should be connected to the same earthing system as the protective device which protects the SWA cable is connected to.
It should not be connected to a separate earthing system.
 
Ok this is all very well and could go on for weeks but please quote the exact wording of the exact regulation that clearly states armour must be earthed at the supply end.

Edit - reply to post #57.
EAWR89:
Earthing or other suitable precautions
8.Precautions shall be taken, either by earthing or by other suitable means, to prevent danger arising when any conductor (other than a circuit conductor) which may reasonably foreseeably become charged as a result of either the use of a system, or a fault in a system, becomes so charged;and, for the purposes of ensuring compliance with this regulation, a conductor shall be regarded as earthed when it is connected to the general mass of earth by conductors of sufficient strength and current-carrying capability to discharge electrical energy to earth.
 
If the SWA was feeding a separated TT installation then clearly the conductive part of the SWA would be earthed from the supply (TN) end,and electrically separated from the earthing arrangement at the load end..

So are you suggesting that the swa would need to be terminated in a separate enclosure before entering a metal consumer unit ( TT earthed) in an outbuilding for example?
 
It does though, if you, read, the law, the installation is under the control of the installer, thus the installation is under the control of the installer, ergo, EAWR applies.
No, the installation is under the control of the householder.
The installer bugged off ages ago and is probably installing other installations, or on here wondering where people get such weird ideas from.
 
No, the installation is under the control of the householder.
The installer bugged off ages ago and is probably installing other installations, or on here wondering where people get such weird ideas from.
You are missing the point the doing of the installation is under the control of the "electrician" no matter where they have been since or after, that job was under their control, they were at work, thus, EAWR & HASAWA applied at that time.
Employed or Self-Employed both apply.
 
It should be connected to the same earthing system as the protective device which protects the SWA cable is connected to.
It should not be connected to a separate earthing system.

So you may end up with a metal consumer unit connected to a TT arrangement with a Zs of up to 1667 ohms for example, fitted adjacent to a metal adaptable box to which the swa is terminated with a Zs of perhaps .35 ohms. Is that right?
 
New posts

Reply to New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
785
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock