ok so if you were to provide your own earth ie rods how many rods would you use or do you keep driving them in until you have a lower enough reading what reading would be acceptable

Minimum of 2 X 5/8'' rods coupled together would always be the minimum number of rods to gain depth and stability. You only need to attain a max of 200 ohms, according to BS7671, but only fools would be happy with such a numbty value!!

Depends what value you obtain with those 2 coupled rods, whether you think it's worth adding another coupled rod or not. Finish off by adding an up front 100mA S type RCD as additional protection to the 30mA RCD/RCBO's....
 

Reply to No earth on installation, WHO is responsible??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
I am doing a new consumer unit install on a second story ex council flat. I’ve notice the mains come in in metal conduit with no CPC. On checking...
Replies
3
Views
1K
So this is 1st floor maisonnette with concrete floor, 16mm2 single insulated tails coming from dual cut out on ground floor, through steel...
Replies
5
Views
867
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
744

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock