Discuss Oven - Kitchen in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
L
lockstock
Hi
I’m installing in an electric oven (3kw) and gas hob, and supplying the power via a double socket which is under the counter ( this is coming off the main ring).
My question is: ‘Do I need to have an isolating switch (for the oven) installed above the counter top’ ?
Many thanks
New circuit to a DP switch above worktop, then from this to your socket of FCU below in an adjacent cupboard maybe.
Thats what I di anyway. Then test and fill out yer EIC then register job with LABC or sheme provider:eek::confused::eek:
Okay thanks for that.
The oven comes supplied with a 13 a plug attached.
I figured that anything supplied with a plug wasn't a fixed appliance , i know that the oven isn't going to be moved, but neither is my washing maching, which is 2.7kw.
But I'll run a separate cable anyway
Fixed appliance is an appliance that is wired direct into the installation via a FCU or similiar, not an appliance on a plug top. So that 2kw does not apply.
These appliances have been developed so that they can be plugged into a ring final circuit. I do agree with Amp David I would rather have a dedicated 20amp supply for these ovens, but there is nothing stopping you just pluging it in, it is after all just a 3kw heater.
Also a BS 1363 can be used as a means for functional switching and isolation provided it can be disconnected under load, which unplugging or switching off can do. As for the part about accessibilty then that is open to interpretation. as it does not require emergency switching then the sockets under the counter could be accessible. Again as Amp David says a switch above the counter top is a better way to design the installation
The point of these applainces are is that you can fit into a normal 13amp socket. The arguement about different circuit, plug into a ring or radial is purely down to convinience and cost.
To run your new circuit would cost. The installation, the mess, having to certify or notify the installation, then testing the circuit, upgrading your bonding which you have to do if it's not to the current specification, RCD fit if the cable is buried, this could cost you a lot.
Plug into your exisitng ring, 13amps is a decent load, and if your washing machine and kettle and oven is on the chances are your 32 amp breaker will trip, so that is the down side.
in that case then it can be run off the ring with a double pole switch above the counter and a plug socket below. If it were my job i would still prefer to put it on a seperate circuit as an oven tends to be on for a while when cooking not like a kettle thats only on for a minute or two, depends on how much trouble you want to go to running a new circuit:)
Agree with all of the above, however, the reason the regs suggest appliances of 2kW and above are on there own dedicated circuit, is to prevent the RFC, that it would normally be plugged into, from being loaded for long periods of time.
Reply to Oven - Kitchen in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Bit of advise if anyone has time.. I have a customer who brought a new kitchen from wrens. Customer has had the route to the kitsch redecorated...