When PAT testing is it necessary to carry out insulation resistance or load/leakage on a Class II (Dummy earth pin) transformer PSU type plugtop? (e.g. phone charger, monitor PSU) Or is just a visual inspection needed?
 
visual only. IR testing L-N would be pointless and could fry the PSU.
 
  • Agree
Reactions: Davisonp
No PATester carries out a live to neutral test (should be linked within the tester). The IR test should be carried out to the metal parts of the outgoing plug using the earth bond lead but always check the testers instructions.
 
  • Like
Reactions: Lucien Nunes
Yes, it is a fundamental safety aspect of the transformer / electronic power supply that it provides adequate insulation between the 230V input and the ELV / Class III device it powers. Therefore an insulation or leakage test to the ELV output is important. Some non-compliant / fake / firecracker phone chargers and their like have deficient insulation that is a smoke paper away from causing a serious shock or electrocution when someone touches the attached phone.
 
Yes, it is a fundamental safety aspect of the transformer / electronic power supply that it provides adequate insulation between the 230V input and the ELV / Class III device it powers. Therefore an insulation or leakage test to the ELV output is important. Some non-compliant / fake / firecracker phone chargers and their like have deficient insulation that is a smoke paper away from causing a serious shock or electrocution when someone touches the attached phone.
might that not fry the device, though?
 
If it does fry it it was never suitable for connection to the mains in the first place. I always test between the mains side to the elv side.
 
  • Agree
Reactions: westward10
very rarely do pat, so i bow to your judgement. problem is, these units usually have a funny socket on the elv side and you can't get a connection with the desparate dan crocs on your MFT.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
~
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
PAT testing transformer plugtops
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
spud1,
Last reply from
telectrix,
Replies
8
Views
4,215

Advert