At this stage the socket outlet is not the prime suspect. The plug-in tester is not a thorough test, however it does indicate that something at earthy potential is connected to the earth terminal. Neutral, earth or anything near either of them is likely to remove the PC leakage current so even if there is a wiring error and no RCD, he would be unlikely to get a tingle. Using the principle of Ockham's razor (the simplest solution is likely to be correct) the fault probably lies in the ground connection to the PC PSU which can be checked easily first, and the socket investigated if the fault is not found here.
FWIW the OP is in Germany so the socket will be Schuko, non-polarised but with reliable side-contact earthing.