At this stage the socket outlet is not the prime suspect. The plug-in tester is not a thorough test, however it does indicate that something at earthy potential is connected to the earth terminal. Neutral, earth or anything near either of them is likely to remove the PC leakage current so even if there is a wiring error and no RCD, he would be unlikely to get a tingle. Using the principle of Ockham's razor (the simplest solution is likely to be correct) the fault probably lies in the ground connection to the PC PSU which can be checked easily first, and the socket investigated if the fault is not found here.

FWIW the OP is in Germany so the socket will be Schuko, non-polarised but with reliable side-contact earthing.
 
Repeat.
The Suckit n See type Tester shown in does not verify neutral earth reversal.
OP describes himself as "new to this".
He also gives a good description of an AC touch voltage appearing on the case of his equipment.
He has asked how to measure what the touch voltage is.
He is new to this.
PLEASE DON'T advice him to carry out live testing with a multimeter

He already has the pc powered up. It is very likely to be leakage current. The basic testing I have proposed exposes him to no more danger than he is exposed to already. I didn't advocate taking anything apart, or measuring at live terminals.

I am a big believer in safe working.
 

Reply to PC-Case conducts energy in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Probably more of a maths problem than anything else / managing to confuse myself. I have been asked to look at energy consumption of some...
Replies
7
Views
531
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock