Discuss periodic, inspection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
have problems with a periodic exam question which carry's 15 marks , they change the questions but the format is the same
graphic was circuit cable coming in conduit to box, connection to L1 l2 l3 cpc
to cable in conduit from motor
question was connection 3 phase motor List five things to be inspected and list sense
I put (isolator which was wrong as it was a just a connection ) scored 40% of 15 marks
Line conductors ~phase sequence is correct ~ sight
Cable termination~ cable are correctly terminated not loose to cause arching ~touch
Cable entry ~ suitable glands /bushes used ~sight
Cable sizes ~cable are correct rating for equipment ~ sight
Accessories isolator~ enclosure is correct ip and fire rating~ sight
thx
I might be tempted to tweak the termination item and split it up a bit more.
Think about the things you might check on an individual cable termination? And even the cable itself on it's way to it's termination.
Cables getting hot FEEL
connections not arcing SMELL
conduit fixing OK FEEL
Yes thats what I put to me they were all visual which what periodic is about
Actually the question says "list the senses" I can think of at least 1 smell, 2 feel
thx
As they are single core cables and they are terminated into a block according to the graphic its hard to expand I could put
Cables ~terminated without strain ~sight
conductors ~ connections of live conductors adequately enclosed~sight
Enclosures ~ securely fixed~sight
Enclosures~ terminals provide suitable protection against mechanical damage~sight
I could go on my answers were not far out, to only score 8 out 15?
how do pass this exam not sure what answers they looking for
thx
For the cables, you could go:-
Cable termination - No excessive bare conductor - Sight
Cable termination - Securely terminated (not loose) - Touch
Cable - Basic insulation undamaged - Sight
Cable - Not under undue strain - Sight
Did mine a few months ago, we were told to look for things like -
Conduit - securely fixed - sight/touch
Conduit - damaged/corroded - sight
Conduit - suitable for purpose - sight
Conduit - incomplete/missing lids - sight
Coupler/Bush - secure - sight
Terminations - secure - sight/touch
Jamie did you do the online version or written
Reply to periodic, inspection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...