hi guys, done a periodic inspection today, obv you reccomend 17th edtion items to them change of db etc etc, but they will never change it.

todays inspection was tt system, with no time delay rcd, the only thing they had was a 30 ma rcd as main switch which controlled all 16 ways.

so therefore if there is a fault one circuit they lose the complete board.

so the 30ma main switch dont comply to 16th as there is no time delay and not 100a.

and now the 30ma rcd main switch dont comply to 17th because there is no discrimination.

i still thought tt systems had to have time delay tho.

whats your views on the above guys how would u go about it??

cheers.
 
Hi, 100ma was to provide a decent disconnection time.
Time delayed was there to stop nuisance tripping.

Where you have a 30ma rcd, this covers both the intention of the 100ma,
and the requirements of the 17th.

This is a very good situation but for the inconvenience part.
to overcome the problem, be it money, or, time, why not suggest a
3hr none maintained emergency light ? just a thought.

In my eyes, you would only need to code the lack of dual circuits ( 4 )
 

Reply to periodic inspection. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
860
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
944
Hi I am installing my first tt system consumer unit I understand that I need a 100 amp time delayed rcd main switch but can I use rcbos in line...
Replies
23
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock