Don't do much three phase and a bit of help would be helpful.On three phase when testing for pfc am I right in saying that I connect the leads to L-N and don't need the earth lead connected. As I'm not sure of putting the meter across all phase, so double the reading that is highest of the three phases. Anyone with a fluke 1561 malfunction testers help would be great. Thanks
 
mcm,
Does the 1651 do phase rotation?
If so it can take the 400V across the inputs, check the instructions to see if it does ph-ph fault current.
These are available from the Fluke website.
My 1653 does, but I can't remember IF the 1651 does as I have not paid any attention to that section in the manual for that meter, sorry.
 
The Manuel is for the 1561-1563 I think it does say something about it but don't want it to go bang. If it is ok would I switch to L-N using f1 and test across L1 and N
, L2 and N and L3 and N then take the highest reading as my pfc.

tester don't do phase rotation.
 
PFC is the highest value between PSSC and PEFC, on a three phase supply this will always be PSSC as L-L PSSC will be the highest, so if the meter wont do this then you must take L-N PSSC and then double it.
 
Il look tomorrow if it does saying it does I test across all phases and take the highest. Does it need to be connected to neutral or earth if a three lead tester or does it normally use two leads L N.

thanks
 
mcm,
Does the 1651 do phase rotation?
If so it can take the 400V across the inputs, check the instructions to see if it does ph-ph fault current.
These are available from the Fluke website.
My 1653 does, but I can't remember IF the 1651 does as I have not paid any attention to that section in the manual for that meter, sorry.

It doesn't only the 1653/4 do
 

Reply to pfc testing on three phase with fluke 1561 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
604
I’m currently doing some testing on some site temps I have a three phase trip system the tails from the head go into a 100 amp RCD which feeds a...
Replies
8
Views
1K
Hello, I'm new to this forum, we are in the process of converting into 12 flats all electric, no gas incl. heating, showers etc. An electrician...
Replies
10
Views
2K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock