Scenario 1
200A Supply into a busbar chamber, this supplies numerous distribution boards but someone has wired a 6mm cable into the busbar which feeds a 20A fused isolator, so potentially you could only draw 20A through the 6mm
Scenario 2
Similarly 100A supply with a 16mm cable which supplies a 63A fused isolator, so the maximum draw is 63A
Scenario 3
32A BS60898 with a 2.5mm cable supplying 1 x switched fused spur, maximum draw is the BS1361 fuse in the spur
Would you have anything wrong with any of the above?
Divided opinions between on our firm
Depends on length of run really as well as the fact that Zs permitted values still need to be met ..haven't enough info for any of the scenario's to be conclusive but all could theoretically comply to regulations.
Well the 32A Zs was too high so it has to be changed and the length of run was 20m max, cable launched above ceiling in armour flex
200A supply on 16mm SWA limited to 63A load, length of run 35m cable tied down a riser, no idea on Zs as unable to test but would presume with the armour and the Zs would be fine
Assuming that in 1 it is the usual arrangement if a busbar with steel trunking for the outgoing cables and the switchfuse attached to that then I see no issue
Assuming that in 2 this is a switchfuses located at the origin with short 16mm tails feeding it then I see no issue
3 however sounds a bit dodgy, if it's a spur from a ring then it'll be ok, but a 2.5mm radial fed via a 32A mcb is unlikely to be ok
In which case I would say both are unacceptable
When you say armourflex what exactly do you you mean?
I doubt it will meet Zs values TBH ...you have the cable length and size so it should be too hard to calculate the Zs ...unless you mean 100amp supply as in your original post?
SY cable, to be honest I thought that was mainly used as control wires not final circuits...
I thought that might be it.
It should be restricted to control circuits or similar where emc shielding is required. But it is increasingly being used for general installation work which is not right
Quick google offers mixed opinions on this, could you expand as to why its not right in your opinion?
The braid does not meet the requirements of an earthed metal sheath/screen in terms of resistance to penetration and it's ability to carry fault current in the case of such a fault.
The sheath is not mechanically strong or resistant to abrasion or other damage.
With specific regards to outdoor installations it is not UV stable or particularly water resistant as you can see once water has got in and green stuff starts to grow under the clear sheath.
Manufacturers data sheets often include words to the effect of 'light duty control and signalling cable not suitable for connection to the public mains supply'
There is another problem which is not the fault of the cable, but another sign of the incompetence of many people claiming to be electricians these days. The cable is often not terminated correctly with the screen often remaining unearthed
SY is a screened control/power cable and it been sold by the wholesalers as a rough service flex which it definately is not, the outer clear sheath does not possess the durability for the enviroments that its been repeatedly put into, its not suitable for outdoors either as its not UV resistant. Many use it as a power flex for 1ph and 3ph extensions where its under constant reeling and unreeling.. the screening and clear sheath suffer and breakdown when this is done and often the screening is not earthed leaving a potential death-trap waiting to happen.. I remove all such cables I see out of service and over the years have found 2 laid across the floor with live braiding because of metal pins or shards had pierced the cable..
Wholesalers are not competent Electricians and it not their job to tell you the limitations of the cable.. its your job to find out before you ever use such a cable.
We are going off topic here but because the OP's is involved in this conversation I'll let him take it back on topic when he feels the need to.
And of course I always seem to catch my fingers on the sharp ends of the braid on the rare occasions I work with it
Haha, in this instance the braid was not earthed, its a 2.5mm connected to a C32A BS 60898 and enters equipment via a TRS stuffing gland, but the internal cpc was used on the plus side
I don't see anything wrong with using sy in certain situations. If the conductors are adequate to carry the current, if the braid is earthed, if the cpc is one of the cores and not the braid itself, if it is installed indoors or away from UV Rays. The braid can just offer a little more protection rather than using T&E , so for some commercial installations it is fine.
The braid does not offer mechanical protection, NYYJ type cable or H07-RNF if flex is required offer far better mechanical protection
The only advantage with SY is the increased emc shielding which is required in control circuits etc
Reply to Preferred Method in the UK Electrical Forum area at ElectriciansForums.net
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...