Discuss Protection on Tncs / tt system in the UK Electrical Forum area at ElectriciansForums.net
cliffed
Supporter
Pme Swa sub main supplying external tennis courts.
Because of cable size,tt system will be installed.
The original Pme supply comes from main distribution area,from a Bill Switchfuse isolator,63 amps.
The new tt system is ze 13 ohms,the Pme earthing system is 0.35 ohnms.
No connection to the Pme system exists in the new install.
The wire netting around the tennis court as zs of 11 ohms.
All main bonding completed
With the metal DB what would happen if the live had an earth fault to the tt system,there is no Rcd protection @ present on the Swa supply.
The sub main if supplied via a TT arrangement will require fault protection via a suitably rated S type rcd.
If your using a TPN DB downstream then I suggest you install DP rcbos as a neutral to earth fault will disconnect an upfront rccb unless you use DP rcbos.
What is the issue regarding cable size?
Assuming his submain is using the PME the s type rcd would have to be at the point it converts to TT.
What size is the swa?
Why is the armour not suitable as the cpc, is it because of extraneous conductive parts at the tennis court building end?
Y
Nothing
Ze of 13 ohm, fault to earth then nothing will happen unless rcd protection is provided. It will remain live as your fault current is about 18A.
yea,16mm 3 core Swa,the main earth bond to the existing building is 50mm earth cable
Nothing
Will look @ Fault charesteristics of the protection device.
Concerned if the fault happen on the tt system,the fuse would not protect.
This is the same problem as with meter tails in an Amd. 3 domestic CU on TT. The only thing that is not protected is the line upstream of the RCD going down to the TT earth. Could solve by putting RCD in separate insulated enclosure at tennis court end so that by the time the cables enter the DB they have local RCD protection. Can't do that in domestic install hence the magic glands etc to minimise risk of short.
Thanks,exactly what I was trying to say.
Reply to Protection on Tncs / tt system in the UK Electrical Forum area at ElectriciansForums.net
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...