Guy from a company we have done a lots of work for over ther years asked me the following today and I didn't really have a good answer since all SWA I have ever had any involvement in installing has always been through a dug trench.

"What are the implications of pulling a SWA through a hole moled through the ground, do we need to duct it first? Will the cable stretch if pulled through directly, i.e with the resistance / friction of earth against its sheath. Is this likely to damage the sheath."

I couldn't really give him a answer I was sure on, hence why I am asking here.

I haven't actually worked out the cable size yet, in fact he hasn't even sent through the Building spec yet for me to determine the size of supply needed.

At a guess on what he has told me for the buildings nature, it will at least be 4 core 25mm pulled through 160m of earth.

What are your thoughts on drag this through the ground with a mole. Would you like to see a duct pulled through first?

I would be worried about a something sharp in the ground binding and damaging the cable, even though according to him they do have some sort of lubricant the mole pulls through first.

Thanks Guys
 
How will you get the warning tape on, and I would be worried about sharp stones . I have never done this, although I have seen them go under the main road and burst the main supply cable at the other side lol.
 
It's gonna be a cow of a pull through 160m in one go.

All of your thoughts about stretching, rough ground and snagging are worries.
How the heck do you install your warning tape as well ???
 
If you hit and damage other services £100 a day will be a bargain, probably quicker too, time you dig the pits by hand ;
 
The cable will be stretched to buggery, as the only way you'll be able to pull it in will be with a tractor or the like!! Forget all about it, it's a fools errand!!
 
His clients site is in the middle of London, they have existing buildings all over and nothing but roadways in between.
He has done it before (so he should know more about it than me!) for them on one of his much bigger projects (that one was too big for me), but he was pulling in 240mm (from his memory) and I know if anything it was further than 160m on that occasion.

I have no idea how he markered it last time, but I do believe they pulled it very deep below all other services in the roadways. Knowing him and his client, Exactly where it is will be heavily documented although no amount of paperwork makes up for no marker imho

The moleing machine pulles it in at a nice slow rate afaik Engineer54, has a camera on it and everything. There is no way anyone would be doing it with a tractor!

The last building he did the M+E was a few million though, it might not be in the budget this time - and it's a temporary building, will be there a few years at most!
 
The mole pllough will feed the cable in as it drives along
but you will not be able to fit the tape half way up
see you tube for video of pipe being pulled in
 
Last edited:
Bloody hell. Do you have any idea what's below the streets of London? - talk about a minefield.

Using a moling machine would be a bit like walking through a area filled with land mines.
 
we pulled a 240 and 300 swa in an open trench at yeovil sewage works used a ford transit van to tow them
the cable stretched and every time i glanded the ends the sheith crept back
 
we pulled a 240 and 300 swa in an open trench at yeovil sewage works used a ford transit van to tow them
the cable stretched and every time i glanded the ends the sheith crept back

Did you replace the stretched cable? Daz
 
His clients site is in the middle of London, they have existing buildings all over and nothing but roadways in between.
He has done it before (so he should know more about it than me!) for them on one of his much bigger projects (that one was too big for me), but he was pulling in 240mm (from his memory) and I know if anything it was further than 160m on that occasion.

I have no idea how he markered it last time, but I do believe they pulled it very deep below all other services in the roadways. Knowing him and his client, Exactly where it is will be heavily documented although no amount of paperwork makes up for no marker imho

The moleing machine pulles it in at a nice slow rate afaik Engineer54, has a camera on it and everything. There is no way anyone would be doing it with a tractor!

The last building he did the M+E was a few million though, it might not be in the budget this time - and it's a temporary building, will be there a few years at most!


Now forgive me if i'm wrong, but you did say ..... "What are the implications of pulling a SWA through a hole moled through the ground, do we need to duct it first? Will the cable stretch if pulled through directly, i.e with the resistance / friction of earth against its sheath. Is this likely to damage the sheath.".... You didn't state at any time that the mole was pulling the cable!!!!

Never used a mole to pull a cable direct, it's always been to pull a duct and draw line ready for a cable, and then only over short spans. I've yet to see a mole pull in a 3 or 4 core 240mm SWA cable over a 160 metres. Not saying it can't or isn't done, just that i have never seen or heard of it. It'll need to be one powerful mole machine to drag that sort of weight behind it, and i wouldn't like to give any odds on there not being any sheath damage either!!
 
Sorry for misleading you Engineer54 - it's hard to remember every detail when posting a new thread. The to and thro questions and answers don't flow like a real life conversation.

I guess I got a little offended by anyone thinking I would even consider using a tractor to instal SWA cable :)
 
Sorry for misleading you Engineer54 - it's hard to remember every detail when posting a new thread. The to and thro questions and answers don't flow like a real life conversation.

I guess I got a little offended by anyone thinking I would even consider using a tractor to instal SWA cable :)

I've seen tractors and all sorts of other site vehicles/plant used to pull SWA cables into trenches and site ductwork!! It really doesn't work very well at all. Most of that cable needed to be replaced for one reason or the other, usually because of visible stretching and sheath damage. God forbid if i ever saw anything like that being done on any of my projects!! lol!!
 
Only ever pulled cable though 6” welded steel pipe. They went under two railway lines and three roads. Four pipes. 3 X 95mm 11KV PILCSWA and a 185mm 3½ core PVCSWA.
I’ll be honest I wasn’t happy about it. But we did use a torque controlled winch and the correct cable stockings.
The bit I was happy about was welding a stud to the end of each pipe and linking them to the MET.

As for PVC serving pulling back, there’s a simple answer. Cut a couple of foot off the pulled end, cap it and let the cable relax for a week. This job took five years to complete, one week was neither here nor there.
 
Been on a job where we pulled cables in with a scissor lifter before. It was over ground, not through ducts/tunnels however and was helped along with regular cable rollers/shoulders. Worked out fine as we took it at a very steady pace. Really took the work out of moving the weight.
 
Only ever pulled cable though 6” welded steel pipe. They went under two railway lines and three roads. Four pipes. 3 X 95mm 11KV PILCSWA and a 185mm 3½ core PVCSWA.
I’ll be honest I wasn’t happy about it. But we did use a torque controlled winch and the correct cable stockings.
The bit I was happy about was welding a stud to the end of each pipe and linking them to the MET.

As for PVC serving pulling back, there’s a simple answer. Cut a couple of foot off the pulled end, cap it and let the cable relax for a week. This job took five years to complete, one week was neither here nor there.

That's basically the only safe way to pull cables through longish duct runs, the correct cable socking for the cable being pulled, along with ample cable rollers/wheels is an absolute must!!. The torque control on the cable pulling winch is set to data given by the cable manufacturer. The torque control acts like a clutch, which will slip the winch drive out as it approaches the dialed in limit(s).
 
When pulling in cables what would be the best way to attach draw wires to SWA? Only had to do this once threw a 60metre ducting with 25mm 3core and we just drilled a hole threw the cable and threaded the rope threw it…is there any other ways ?
 
The best people to speak to would be the "Molers"

A. To see if they are prepared to risk moling in previously bombed ground, with or without the customer paying for damage to the mole
B. To get thier opinion of pulling such a cable with the mole and have they have done it before.
 
The best people to speak to would be the "Molers"

A. To see if they are prepared to risk moling in previously bombed ground, with or without the customer paying for damage to the mole
B. To get thier opinion of pulling such a cable with the mole and have they have done it before.

He is going to ask the "molers". He just wanted my opinion, and I wanted yours :)
 
When pulling in cables what would be the best way to attach draw wires to SWA? Only had to do this once threw a 60metre ducting with 25mm 3core and we just drilled a hole threw the cable and threaded the rope threw it…is there any other ways ?



Exactly what were talking about, ....There are many way's to attach a pull wire to a SWA cable and the like. Most of them will cause damage to the cable being pulled, depending on how much stress is applied to the pulled cable. The correct method is by use of a correctly sized cable socking that will tightly grip the pulled cable over about a metre of the cable length.
 
pulled long hv cables used long stocking then drilled 2 holes through cable sock and cable (at different angles )then bolted sock to cable and taped up well
 
As said Elliot, use a cable sock. If its put on right it won't pull off. The more pressure you exert it just gets tighter.
If you don't have a sock, a series of loops and half hitches works very well.
 
it came from a rep. from cable manufacturers it also helps with the stress/stretching of cable ,also recommended in australia after cable fell 16 floors in a riser (is your mind still boggling)
 
it came from a rep. from cable manufacturers it also helps with the stress/stretching of cable ,also recommended in australia after cable fell 16 floors in a riser (is your mind still boggling)

It will do absolutely Nothing to alleviate stretching or reduce stress of a cable....

I'd like to see that recommendation, a cable sock actually works better the more weight you are pulling on. So either the sock wasn't of the correct size for the cable being lifted, or was of the wrong grade of steel for the weight of cable...

I have never seen at any time or circumstance the need to bolt a cable socking to the cable. Kind of defeats the whole purpose of the cable sock too, when you think about it!!!

So Yes, the minds still boggling!!
 
Last edited by a moderator:
SAFETY ZONE
ALERT
3 March 2010
www.cfmeu.asn.au
CABLE PULL FAILURE
Background
Recently on a construction site in Perth’s CBD the electrical contractor was in the
process of pulling a 50mm Diameter fire rated cable from basement 2 to level 21.
The pulling “sock” which was attached to
the end of the cable slipped off, causing the
cable to drop from level 16. It started to spool on the ground floor and basement 1.
All entry points to the riser had been bunted
off and signage displayed stating activity
occurring.
No one was injured from the incident.
Cable was in no state to be used and was recycled.
Root Cause
The cable’s orange shield had stripped away
from where the sock had been placed
on the end of the cable. Refer to photos.
Corrective action
Cables now are required to be spliced and shackled to pull line, in addition to pulling
sock bolted through cable. Ref photos.
View of orange shield stripped away from 50mm fire rated cable.
View of corrective actions, shackles atta
ched through cable splice to pull line as
secondary safety control as well as sock bolted through cable
 
You wouldn't happen to have the photo's of the ''root cause'' would you.?? Never heard or seen the PVC outer sheath being ''stripped off'' a cable being pulled via a cable sock....
 
How does it help with the stretching of the cable? Daz
 
Don't worry just found the photo's myself!!

I've seen exactly how they want the socks to be attached to the cable as well. Oh dear, whoever thought that system up needs to be re-educated or has no conception on using the cores as a part of the pulling medium!! As for bolting the far end of the socking to the cable!! lol!! This is a union report is it not, so nothing actually official then, which is just as well!!!



One has to wonder how did the Aussie's pull cables up riser shafts in the past, and in considerably higher buildings than 16 storey too and didn't seem to have much of a problem doing so either.

Funny that it's taken them until 2010 to find a (non existent) problem that's actually never been a problem before. Well not to any statutory body anyway!! Take this so-called report with a large pinch of salt, it's a floored report!!
 

Reply to Pulling SWA through a moled hole. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
559
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
489
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
3K
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
930
So I had a ceiling repair done in my bathroom due to water damage. The neighbors toilet above me was leaking for who knows how long. Mold...
Replies
1
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top