On an Installation Cert in the 'Max Permitted Zs' column should i put the tabulated values in the regs or should i put the corrected values(x0.8 rule of thumb)????
My guess would be corrected values as that would be max zs at ambient temperature at the time of test?
Cheers peeps,
Dan:cool:
As I understand it, you are expected to put in the uncorrected tabulated values from BS7671.
If thes are NICEIC or Napit forms, I believe you are also expected to put in the uncorrected measured values.
Bit weird, but that's the scheme providers for you.
general opinion is to enter the brb ( uncorrected ) figures on the test sheet, but the readings you get should be below the corrected figures. very rare to see cables reaching max. temp. of 70 deg. anyway
but if it's a TT system with RCD protection, you can enter 1667.
Reply to Quick Question - Max Permitted Zs Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...