It seems strange to me that a double socket is only rated to 20A (not commonly known) when you theoretically could have 26A plugged into them. Clearly it works this way, otherwise there would be fires left right and centre, but it does feel like there is an element of chance involved.
The British standard requires that a twin socket be tested with a load of 20A made of of a 13A load and a 7A load. Manufacturers are free to make the total current rating whatever they like above this.