Discuss Rcd and fuses in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi sorry a basic question.
I have no regs books and I’m still learning.
on a eicr would a board with no mcb e.g rewirable fuses be unsatisfactory c2/ or c3 or is it fine as long as it makes disconnection times.
also same with no rcd does this fail now as their most likely will be a circuit passing a bathroom or sockets that could be used outside.
rewireable fuses IMO would be a C3 if disconnection times were OK. could even be a C2.
as for RCD.. sockets for outdoor use, no RCD is a C2. other sockets usually a C3. bathrooms C3 if supplementary bonding is in place, otherwise a C2.
cables buried in walls< 2" deep, no RCD is a C3.
lighting circuits with no RCD is now a C3 under 18th Ed.
think that just about covers it.
the reason i may give rewiereable fuses a C2 is potential danger if a donut replaces fusewire with one of a higher rating. this is common, esp. with farmers who often use an offcut of barbed wire as a 30A fusewire.
Okay great thanks.
Just what did you mean by could be a c2 for non mcb.
What do you think needs to be considered if at all with BS3036 fuses as this means of protection is still recognised by BS7671.
Reply to Rcd and fuses in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...