Discuss RCD Testing - Remove devices prior to testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
dazj90
I've got a 3 phase DB with individual RCBO's supplying various equipment, Fire Alarm Controller/Water Heaters/Office Sockets/Office Lighting/Air Conditioning Controller.
GN3 suggests "Any load or appliances should be disconnected prior to testing", would it be ok remove the supply at the RCBO for this and is it necessary to remove the load?
Would removing the fuse from a spur be sufficient enough to remove the load as there are a couple of circuits that feed a spur then the device.
Full arc flash gear will be worn under companies rules.
Yes removing the fuse would be sufficient, or just switching the spur off if it has a switch.
I do not believe there is a standard form for quarterly RCD testing.
I would either create your own form or modify say a minor works certificate to an RCD testing report.
Something like this depending on what you need to report
  • RCD quarterly test report.pdf
Reply to RCD Testing - Remove devices prior to testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...