Discuss RCD throwing Zs readings off in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
installed a new dual rcd cu today and on completeing my tests I noticed the zs values were slightly above the max permitted by bs7671.
All my other readings, r1+r2s ect were fine and the ze was 0.2 off the top of my head.
took a zs reading off the load side of both rcds and both values came out around 1.03.
rcd funcional tests were fine and so too were the tripping times.
my question is, i'm i ok calculating the zs values and making a comment on my cert such as, "zs values calculated as rcd falsifying readings" ?
thanks guys
If your circuits were all protected by 30mA rcd/rcbo's then your maximum Zs can be taken as 1667 Ohms-just record the values exactly as they were measured.
last week i had an RCD giving Zs as 341ohms when Ze was 0.16ohms!!!!! so you're not doing badly .
off course! feel stupid for overlooking this now! :eek: would you still throw a little comment in explaining that zs values exceed that permitted for mcbs but circuits protected by rcd, or just assume that he who next looks at the cert should know why the values are good?
It can't do you any harm to add a little note.
Reply to RCD throwing Zs readings off in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Gents. I did some earth loop tests on Rolec power pedestals (2x 16 amp outlets) that are harbour side, looped in and out from one another. Three...