Yep, but if there happens to be 9mA leakage and your ramp test shows a pass at 22mA then you will leave a non-compliant RCDin service thinking it's okay.
You have to remember why I did the ramp test, which was to see if it was over sensitive rather than insensitive.
You've made me think though - I'm wondering why my assessors have never pulled me up for not switching off all unecessary circuits (eg.lights) when I do an Auto RCD test with my MFT. I tend to use the cooker circuit and switch off the ring(s) - doesn't do fridges any good! Is it because the standard auto test doesn't include a ramp test? When the tester leaks 30 mA does it take account of existing leakage?