Yep, but if there happens to be 9mA leakage and your ramp test shows a pass at 22mA then you will leave a non-compliant RCDin service thinking it's okay.

You have to remember why I did the ramp test, which was to see if it was over sensitive rather than insensitive.
You've made me think though - I'm wondering why my assessors have never pulled me up for not switching off all unecessary circuits (eg.lights) when I do an Auto RCD test with my MFT. I tend to use the cooker circuit and switch off the ring(s) - doesn't do fridges any good! Is it because the standard auto test doesn't include a ramp test? When the tester leaks 30 mA does it take account of existing leakage?
 
When the tester leaks 30 mA does it take account of existing leakage?
Nope, the tester isn't that clever. If it applies a 30mA leakage test the actual leakage seen by the RCD will be the test leakage plus any other leakage from circuits and appliances.

Ideally you should disconnect all circuits and all loads from the RCD when ramp testing it.

It's good you're beginning to think about the bigger picture, it might help if you draw some circuit sketches of the possible fault paths and testing procedures.
 

Reply to RCD tripping. Give me a clue! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top