Tommy29
I have isolated the MCB feeding my garage when switched on trips the RCD. There is no load on the garage I have an internal switch in the garage that switches all circuits off. So the fault must be between the MCB and the garage switch. The armoured cable is under the patch so to dig up would be horrendous. Could it be a faulty MCB?
In short, the chance of this fault being a faulty mcb is so small, it’s verging on the impossible.
All this wet weather lately if I had to guess I would say water ingress is most likely.
You need an electrician to insulation test it first .
At least you will have a definite answer.
Thanks that’s what I has thought. I have checked insulation between Earth and Neutral and there is no indication of a short. I did not megger it only a multi meter.
Highly unlikely to be an mcb. I'd get someone to do a bit of testing for you, as changing random parts such as the mcb would be false economy. Is the switch in your garage single or double pole? If only single the fault cou,d be upstream of that rather than underground. But again testing would find this out.
You haven't 'checked insulation' just lack of continuity. Multi meters tell fibs to the uninitiated, when it comes to IR. Needs L involved, too.
I'd be inclined to say you have an earth to neutral fault somewhere. As said above, wet weather. Has anything in the installation changed recently?
If the SWA cable is in fact under the patio, then the cement holding the paving down could have eaten through the cable. It happens!
15 minutes work, disconnect swa from both ends.
IR test the cable.
You will then know if the fault lies with the cable or in the garage installation itself.
At a guess, if it’s a normal garage with a socket circuit and a lighting circuit only, I would expect a decent spark that is used to fault finding should have a diagnosis within an hour.
If it’s an easy to find one, probably have it diagnosed and fixed within the hour.
As davesparks stated the cement is highly unlikely to damage the cable. I've seen people get chemical reaction burns from cement/concrete its nasty stuff if it gets on your skin and reacts.
Reply to RCD TRIPS BUT MCB DOES NOT in the UK Electrical Forum area at ElectriciansForums.net
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...