- Reaction score
- 1
hi all
my parents just bought a new place and the electrics are dodgy to say the least,
one circuit in-particular is giving me a headache, okay here's the set up
The supply is TNS and the consumer unit has one 30mA rcd covering half the circuits,
the circuit that is causing problems is a 20amp mcb on what looks like to be a ring
or maybe a lollipop,
my brother was complaining that when he plugged the play-station in it tripped the rcd, so i thought it was polarity problem,plugged socket and see in and it showed ok then i isolated the circuit and had a look behind the socket, all connections were tight and cpc sleeved,fixed the faceplate to socket and plugged the play-station in as soon as the plug was connected to the socket the rcd tripped even though the mcb was still in the off position???
i think this is an accumulation of neutral to earth current a bit like when you snip neutral and earth and the rcd goes on a dead circuit,
going back this weekend to do insulation test ,earth leakage and rcd ramp test
also i noticed that one leg of the ring was in aluminium and the other half copper
anyone came across this fault before? and would a play-station plugged into a circuit with the mcb off contribute to accumulation of leakage
forgot to say this also happens when the xbox or hoover is connected
any advice appreciated