A fault downstream of the two RCDs will trip either or both.
A fault in between the two would only trip the upstream one. (This is why we place the RCD at the origin of the circuit in special locations.)
I would suggest that the next time the RCD/s trip, they switch off all the MCBs in the caravan, then reset the first RCD, then the second RCD, and if both reset, switch on each MCB untill the fault returns.
If they are able to identify the MCB where the fault occurs, then they should attempt to identify whether it is an appliance or a fault in the circuit causing the fault.
Disconnect or turn off each appliance, reset the MCB etc.

This is what i was telling them.to.do over the phone. Told him turn off all MCBs turn on all RCDs and turn it on one by one. He said he did that and there was no power at all, nothing tripped but no power. RCD in caravan blown? Doubt it, think its just him. But when he turned caravan sockets on after a couple of seconds outhouse RCD went. There i think is the answer.
They think the fault is in between the RCDs but im telling them its not, its in the caravan.


Sent from my GT-I9100 using Tapatalk
 
This is what i was telling them.to.do over the phone. Told him turn off all MCBs turn on all RCDs and turn it on one by one. He said he did that and there was no power at all, nothing tripped but no power. RCD in caravan blown? Doubt it, think its just him. But when he turned caravan sockets on after a couple of seconds outhouse RCD went. There i think is the answer.
They think the fault is in between the RCDs but im telling them its not, its in the caravan.


Sent from my GT-I9100 using Tapatalk
standard practice this.....just introduce circuits 1 at a time until the RCD lets go....then its a case of appliances on that circuit......
 
they need to know what is at fault so they know what to rob next.
 
It diesnt matter about pay,its council work so its through my company, and to be fair theyve been nice as pie to me so far so no complaints, its just trying to explain to them that its in there caravan because once its past the service cable going in there its nothing to do with us.

Sent from my GT-I9100 using Tapatalk
 
Yep, as soon as any current flows through the RCD it would trip with a N-E fault even if the live of the faulty circuit is isolated.
 
It diesnt matter about pay,its council work so its through my company, and to be fair theyve been nice as pie to me so far so no complaints, its just trying to explain to them that its in there caravan because once its past the service cable going in there its nothing to do with us.

Sent from my GT-I9100 using Tapatalk
well they might come across as all sweetness n light simon but dont you let your tools out of your sight mate......and i wouldn`t let on about whats in the van either.....sneaky light fingered little opportunist gets these are mate.....dont lose sight of who and what they are mate.....
 

Reply to RCD's inline in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
331
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
374
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
850
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
296

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top