Hi, Just recently qualified.
I've replaced some old 32amp junction boxes under the floor in my landing with Wago and Wago boxes to make them maintenance free prior to putting down new flooring.
Prior to doing this, i tested the ring continuity, r1 was 0.52 ohms, rn was 0.53 and r2 was 0.73, so was well within the 1.67 reg, now when i tested the ring once the work was complete the readings are: r1 0.47, rn 0.48 and r2 0.99 ohms. I have double checked all connections, but the r2 reading still seems a little high and doesn't meet the 1.67 guideline. I/R tests are fine. Maximum Zs is 0.54 ohms but that is on a dropdown spur to the lounge from the ring upstairs.
The reason i changed them was that there was no earth sleeving present and the terminals where not tight and could not be tightened.
I know the Wagos will introduce more resistance but just wanted to check what you guys thought.
Timmo.
 
Can you still get to your new connections to split the cpcs there and check continuity at that point.
 
Hi, Just recently qualified.
I've replaced some old 32amp junction boxes under the floor in my landing with Wago and Wago boxes to make them maintenance free prior to putting down new flooring.
Prior to doing this, i tested the ring continuity, r1 was 0.52 ohms, rn was 0.53 and r2 was 0.73, so was well within the 1.67 reg, now when i tested the ring once the work was complete the readings are: r1 0.47, rn 0.48 and r2 0.99 ohms. I have double checked all connections, but the r2 reading still seems a little high and doesn't meet the 1.67 guideline. I/R tests are fine. Maximum Zs is 0.54 ohms but that is on a dropdown spur to the lounge from the ring upstairs.
The reason i changed them was that there was no earth sleeving present and the terminals where not tight and could not be tightened.
I know the Wagos will introduce more resistance but just wanted to check what you guys thought.
Timmo.


The 1.67 is to give you a rough idea of what your r2 is likely to be if using 2.5/1.5mm2 cable. As long as your Zs is OK, don't worry.

Jay
 
Yeah that's what NAPIT Tech said. I'm putting the flooring in now, Thanks for the replies.
 
  • Like
Reactions: Zdb
oh sorry, what Jay said:
The 1.67 is to give you a rough idea of what your r2 is likely to be if using 2.5/1.5mm2 cable. As long as your Zs is OK, don't worry.

Jay
 
[QUOTE="...
I know the Wagos will introduce more resistance ...[/QUOTE]
You shouldn't have any measurable resistance across a Wago.
 
  • Like
Reactions: SparkyChick
His R2 has increased by 0.26 since he reconnected why is this something not to worry about.
 
maybe where the old junction boxes had the cpc twisted together prior to being in the terminal made for a better connection than the wagos, there where 4 junction boxes replaced.
 
THeres a video on YouTube testing wago connectors for resistance and you'll be surprised at how little the resistance will change. Your meter may not even pick it up.
 
No the Wagos would not have caused this, me I would want to find it unless your original reading was incorrect because the R1 has gone down.
 
surely if the terminals were not tight on the line and neutral in the old junction boxes then the wagos would be a better contact and therefore the r1 + rn goes down by 0.05 ohm. As I said I have double checked all connections, i did replace about 2m of old cable with new, but im sure that wouldnt cause it.

Thanks again for the replies.
 
As said above, I wouldn't worry about it too much if the r1 and rn readings are the same and the r2 is a bit higher than expected especially if the Zs reading is well within it's limit for the protective device.

When the battery in my Fluke mft are low the leads don't always "zero" which increases readings. Als,o a good squeeze on the croc clips when testing can bring the reading down by 0.05 ohms. Other factors such as ambient temp etc may effect your test readings.
 
My jb's are maintenance free ( Dave tight), you know the old saying , if it aint broke don't fix it.
 
  • Like
Reactions: tomspark93
I prefer the Hager J803's MF boxes to using a wago box personally. I only tend to use wagos in light switches.
 
I prefer the Hager J803's MF boxes to using a wago box personally. I only tend to use wagos in light switches.
I used the J601, on lighting circuits.
 
  • Like
Reactions: LankyWill

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Replacing old junction boxes with Wagos
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
Tim Brennan,
Last reply from
7029 dave,
Replies
16
Views
5,310

Advert