Hi all I am about 2 years retired after being NICEIC registered for over 20 years.
An old customer just a little concerned about an EICR just been done on her property by someone else now with lots of N/A everywhere

main one being no end to end readings (R1R2) entered for the ring circuits

I can’t think of any reason why these would not have been entered. Any ideas apart from laziness
 
Hi all I am about 2 years retired after being NICEIC registered for over 20 years.
An old customer just a little concerned about an EICR just been done on her property by someone else now with lots of N/A everywhere

main one being no end to end readings (R1R2) entered for the ring circuits

I can’t think of any reason why these would not have been entered. Any ideas apart from laziness

Lack of R1/R2 for rings is normal as CPC continuity is confirmed by the r2 test, as is respective continuity for r1 and rN.

The form only requires one of R1/R2 or R2 both of which can be calculated from the little 'r' readings and, as those are measured results, this is perfectly acceptable.

So as long as all the little 'r' ring continuity tests are complete and compliant then the big 'R' results will be.
 
confusion reigns . OP.... end to end is r1,r2,rN. note lower case letters. the EICR should have r1,r2, rN for a ring. all circuits should have either R1+R2 or R2 readings entered on the test results.
 
  • Agree
Reactions: loz2754
confusion reigns . OP.... end to end is r1,r2,rN. note lower case letters. the EICR should have r1,r2, rN for a ring. all circuits should have either R1+R2 or R2 readings entered on the test results.
Thanks for your replies. I missed that and have always entered r1, r2, rn all lower case as you say. I’ll just go back to my armchair and sleep.
 
  • Like
Reactions: DPG
Thanks for your replies. I missed that and have always entered r1, r2, rn all lower case as you say. I’ll just go back to my armchair and sleep.
i'm already in mine but can't sleep. she's not brought me my beer yet.
 
  • Like
Reactions: DPG and dogtag
Sounds like a job done to a standard which is commonly encountered nowadays. I always do the full figures and as for N/A everywhere, was that agreed with the client/person ordering the work? Did it say as much in the certificate? Those sort of certificates are a pale comparison to an EICR done properly. I think we know in the trade that these kind of things are laziness or a lack of knowledge/pride in ones work. They do leave themselves open to various law suits if things go wrong. As well I worry about the client accepting this as satisfactory as they may have things wrong with their installation that have not been properly investigated/remedied.
 
  • Like
Reactions: loz2754 and dogtag
What's wrong with the word "Obscured"?
 
It certainly seems to be, but to me "redacted" means removed, what we are generally asking is for information to be "obscured" just seems to be a fad, someone used it and others have thought "Oh nice word" I'm going to use that and latched on I suppose.
 
  • Agree
Reactions: DefyG
You need a Walther PPK for that.
 
  • Winner
Reactions: loz2754
A friend of mine in France belongs to a shooting club and has a Glock, I was amazed how lightweight it was and accurate, I think most of that was down too how little recoil it had when shot, the barn door was in jeopardy.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ring circuit readings
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
dogtag,
Last reply from
Mike Johnson,
Replies
16
Views
2,556

Advert