Discuss ring circuit test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

W

waitees

Hi all

just wanted to confirm as got the nic man and anything that comes up, want to be confident in the answer.

Am i right saying that the r1 & r2 reading on a reading circuit should be ruffly the quarter of the end to end readings added up ie

L2L=0.26
N2N=0.26
L2L=0.43

TOTAL = 0.95

THE R1 & r2 value should be ruffly a quarter of that total.

also another quick question on the cert it says refernce method i have looked at the bs7671 bit confused, which one is mostly used in a domestic property ?

any ideas ??:confused:
 
Hi all

just wanted to confirm as got the nic man and anything that comes up, want to be confident in the answer.

Am i right saying that the r1 & r2 reading on a reading circuit should be ruffly the quarter of the end to end readings added up ie

L2L=0.26
N2N=0.26
L2L=0.43 earth 2 earth?

TOTAL = l2l + e2e devided by 4 is your r1 plus r2 at each socket

THE R1 & r2 value should be ruffly a quarter of that total.

also another quick question on the cert it says refernce method i have looked at the bs7671 bit confused, which one is mostly used in a domestic property ?
Mostly clipped direct mate
any ideas ??:confused:[/QUOTE
 
ref method means how is the cable installed, ex ref c is clipped direct to wall not touching any insulation. ring test. end to end all 3 conductors, results are little r1 little r n and little r 2. just do more study
 
measure end to end of both cables
l - l =r1
n - n = rn
e - e =r2
cross connect l - n
(add together readings r1 + r2 and divide by 4)
this reading should be seen around ring and will become R1+R2
 

Reply to ring circuit test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
824
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock