What mechanical insulation are your referring to, I would check across all lines and neutrals, had it so many times with lines and cpc's mixed up, doesn't take long and can save you chasing your tail for a fault that is very easy to find, if you check and all ok, then start breaking down the ring.
 
I'll tell you how i do it, without the hassle of dragging wander leads all over the gaff.

Remove all the plugs from the sockets in that circuit. connect one leg only of the offending component of the ring, perhaps an earth in your case and then go round with a typical three neon socket tester and find out at which point you go from earth fault to a good reading. Then connect the other end and do the same in the opposite direction - you will narrow down the fault in no time.

If the fault is within an FCU on the ring main, you will also be able to narrow this down too.

Then do the same for your line circuit.

I have used this method loads of time and it is much quicker than pulling the wander lead around.
 
I'll tell you how i do it, without the hassle of dragging wander leads all over the gaff.

Remove all the plugs from the sockets in that circuit. connect one leg only of the offending component of the ring, perhaps an earth in your case and then go round with a typical three neon socket tester and find out at which point you go from earth fault to a good reading. Then connect the other end and do the same in the opposite direction - you will narrow down the fault in no time.

If the fault is within an FCU on the ring main, you will also be able to narrow this down too.

Then do the same for your line circuit.

I have used this method loads of time and it is much quicker than pulling the wander lead around.

Hi,

Thanks for that, FAA.

I've already ordered a Kewtech ACC50MTL from ISSWWW, which should be here hopefully tomorrow. Like I say it'll come in handy for testing bonding etc anyway..

I'm with ifindoubtdont's on this too. The whole installation will need testing anyway just by what's been discovered.

1) Shower keeps tripping after about 10 mins (9.5kw) 41.3amp on a 32amp breaker, 6mm conductor. Testing shows 36amp is being drawn, though I may get away with a breaker with larger over current protection.

2) Grouped cables above a door standard, poorly terminated in block connectors (too much of the conductors showing), and the sleeving missing from the cpc's!

3) A double surface box fitted directly in front of an outside vent!!

4) An unused light switch point covered with wallpaper (live conductors behind).

5) Pulled off a splash back in the kitchen and there's another exposed point with live conductors freely sitting with no connectors.. Bizarre!!!

6) A spur taken from an unfused spur supplying kitchen unit lighting!

7) Ring final circuit no longer a ring!....

And that's just sor far!!

So Thursday is going to be a busy day!! :-/
 
if its one of these jobs worth checking gas/water earth ok/ie; not short ends just stuck under the wallpaper!
have had a lot of them !
 

Reply to Ring Final Circuit Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
838
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock