Just completed 15 new builds and on 3 properties the main bonding was run through the pvc sleeve which the gas pipe runs through the caverty wall to the meter outside.
Have now been told that they may not connect the gas meter to those properties unless the bonding is re-routed.
Cannot find any reg thats states you cant run the bonding this way only found this one:
BS6891-2005
8.16.2 Separation of installation pipework from other services
Where installation pipes are not separated by electrical insulating material, they shall be spaced as follows: a) at least 150 mm away from electricity meters and associated excess current controls, electrical switches or sockets, distribution boards or consumer units;
b) at least 25mm away from electricity supply and distribution cables.
Sates distribution cables nothing about bonds. Any one shed any light on this please
BS6891-2005
Try bonding the gas pipe when you're not allowed to go closer than 25mm.
That would be a good trick :D
i'm doing the wiring regs at the moment and i do have some vague recollection of having heard or read somewhere that there should be a minimum distance between main protective bonding and the service pipe with regards to route - certainly that it is not allowed to be clipped to the pipe.
However, just had a look through the regs and can't find anything at all - section 528.3 should be favourite "Proximity to non-electrical services" but nothing. Not looking too good for my 2382 exam !!!
The sleeve of the gas pipe is not a permitted roue for the bonding cable
Now where I got that from is anybodys guess,it has just been my understanding for many years
It is possibly more to do with the gas regs than electrical
I hope I am wrong,but I wouldn't bet on it
Try the plumbers forums for a water mans view
I was thinking about this last week, as I had to run gas and water bonding together beside the the gas pipe. Reg 528.3 did come to mind, but I rejected it due to the obvious need to connect the pipe for the gas bonding, and the the subsequent consideration that the gas and water BOTH go to the MET anyway. Lastly, under fault free conditions the bonding will have no potential difference to the gas pipe, and then I came full circle and thougth ..... well that's the whole point anyway!
So I did it.
I heard about something like this, your not even supposed to cable tie your bonding cable to the gas pipe. I can't remember for the life of me where this was written or who told me :(.
found it
Main bonding conductors should not be supported by the service pipes they are connected to,Reg 543.3.1
I usually put a sneaky zip tie just before the clamp just to stop the cable being moved, a bit like a cord grip, so shoot me :D I clip it to the wall up until this point though ;)
Reply to Routing main bonding alongside gas pipe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...