Hi all, looking some advice on s type rcds. Basically can you use them on tt installations for earth fault protection on circuits that don't require additional protection? Know that on a tt installation disconnection times of either 0.2 sec or 1sec must be achieved depending on circuit, but with the delay on the rcd will they be achievable?
Appreciate any advice, thanks!
 
Hi all, looking some advice on s type rcds. Basically can you use them on tt installations for earth fault protection on circuits that don't require additional protection? Yep.
Know that on a tt installation disconnection times of either 0.2 sec or 1sec must be achieved depending on circuit, but with the delay on the rcd will they be achievable? Wont make any diference , disconnection times are for the mcb.
Appreciate any advice, thanks!

Regards Pete.
 
Hi all, looking some advice on s type rcds. Basically can you use them on tt installations for earth fault protection on circuits that don't require additional protection? Know that on a tt installation disconnection times of either 0.2 sec or 1sec must be achieved depending on circuit, but with the delay on the rcd will they be achievable?
Appreciate any advice, thanks!


Let's say it would be prudent to have an up front S type RCD as additional protection on a UK domestic TT system!! lol!!

30mA RCD protection on TT systems are not classified as additional protection, They are a Prime means, as they are generally the ONLY means of achieving TT system max disconnection times. It is the RCD that will disconnect the supply under earth fault conditions, NOT the MBC as has been indicated above....
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
s type rcd
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
copey84,
Last reply from
Engineer54,
Replies
2
Views
1,969

Advert