robmark1976
Hi hope you can help, we have just carried out a survey of an office floor that we are due to fit out and the floor boxes and VAV units don't have separate Earth cables to them, even though there are numerous circuits the earth relies on 1 earth cable bolted onto the metal trunking by the distribution board and then linked to all the different circuits and not separate earths, I know this does not comply with BS7671 but the consultants wants me to be detailed and quote the regulation from the REGs to show this does not conform, Thanks Rob
the metal containment can be a common cpc for all circuits contained within it.
I thought all individual circuits had to have there own PC and not share an earth with other circuits or am I wrong?
Not when a full metal containment system (eg, trunking and conduit) is being used to distribute several circuits within....
I'll put money on that metal containment providing a far better Zs value than your 1mm and 1.5mm separate CPC's.
A very good illustration of the dangers of being self appointed electrical police without knowing the regulations or even where to find the appropriate regulations. Humble pie beckons.
Now i wonder WHY the project consultants want you quote the regulation from BS 7671?? Because they already KNOW there isn't one, and that there own site survey has already confirmed compliance maybe??
Hi hope you can help, we have just carried out a survey of an office floor that we are due to fit out and the floor boxes and VAV units don't have separate Earth cables to them, even though there are numerous circuits the earth relies on 1 earth cable bolted onto the metal trunking by the distribution board and then linked to all the different circuits and not separate earths, I know this complies with BS7671 but the muppets in suits wants me to be detailed and quote the non-existant regulation from the REGs to justify their existence, Thanks Rob
correction applied for you
Reply to Seperate Earthing circuits in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
I've just started at a new church and the electrics are bit of a shambles. I'm not going to be touching them as I'm not qualified, but one thing I...
5K
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
6K