Hi all,

A customer doesn't want a new consumer unit, but wants work doing to an existing lighting and existing ring circuit.

I believe I'm correct in thinking that if I do work on these older circuits, I must then RCD protect them. Is it better to fit an RCD to the incoming mains, before the fuse box, or individually RCD protect each of the two circuits?

Many thanks

EW
 
if you are goin to rcd the whole board you will need to also fit a main switch before the rcd. I would fit rcbo's on the individual circuits. It will stop nuisance tripping of the whole board.
 
if you are goin to rcd the whole board you will need to also fit a main switch before the rcd. I would fit rcbo's on the individual circuits. It will stop nuisance tripping of the whole board.

Sounds like a plan. I'm assuming I can get push in RCBOs to replace the fuses?

Regards
 
You cant get RCBO's to replace push in's.........probably best fit a small enclosure alongside the DB with a couple of RCD's in .
 
if you are goin to rcd the whole board you will need to also fit a main switch before the rcd. I would fit rcbo's on the individual circuits. It will stop nuisance tripping of the whole board.

Why do you say that he needs to fit a main switch before the rcd ?
 
As an rcd should not be the main mean of isolation for the installation.

I spoke to NICEIC yesterday, and he cited the regs, saying that there is provision in the regs for using an RCD as a main switch.

Seems to be a bit of confusion around this area. :confused:
 
yes you may have an rcd as a main switch see the regs for tt systems shud clarify the situation cheers ceri
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Single main RCD or multiple
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
EWebster,
Last reply from
cegsdj,
Replies
10
Views
5,332

Advert