Discuss Some MFTs have PSC/PFC test combined, I wonder why others have it as a separate test in the UK Electrical Forum area at ElectriciansForums.net

In "no trip" mode my DL9118 does high current L-N and low current L-E on the one test, afterwards you can press the top 'function' key and it toggles between the Zs/PFC and the Zsupply/PSCC results.

In high current mode it only measures the one you select, which is odd.

My suspicion is it makes some use of the PSCC data to help with the no-trip test, but there is nothing said about any of that in the instruction book, etc. For example, with the 3 wire connection while you measure the L-N drop you could also measure the N-E rise to get some idea of R1 and Rn separately (at least as far back as the N-E link point in the distribution system), and it might help when you do the L-E test to get some idea of R2 by knowing R1 from the first test, etc. But that is speculation!
 
I can't explain it, I have to do a double take and make sure it wasn't just a one off, and it wasn't. I got different results and I have absolutely no idea why.
What scale of difference do you see?
For me the readings are generally slightly higher on the L-N setting, using the same lead and simply moving the plug. We are talking 0.05 ohm variation at most.
The readings on both settings are however slightly inconsistent in their own right; 10 tests in a row with suitable pause between each one also yields variation within a 0.05 ohm window.
The N socket on mine has had considerably less use and I also wondered if it might simply have more tarnished contacts!
 

Reply to Some MFTs have PSC/PFC test combined, I wonder why others have it as a separate test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
644
Because none of us are beyond schoolboy errors.......... Doing some events kit testing over the weekend, some larger metal stand distro panels...
Replies
7
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
834

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock