Fault finding. Good to systematically and logically investigate the problem, then the culprit has been staring you in the face...

phone call from new customer- no power.
get there, split rcd board. “It’s that big switch that won’t stay up”, says the woman
Ok, the rcd. Unplugged everything I could find, did some initial dead tests... everything seems ok. Powered up RCD, it holds... turn on each mcb in turn... all holding... Great!

Two minutes pass, then click! First mcb trips, downstairs sockets. Damnit.
Wasn’t the rcd at all, was the mcb!

She’s on the phone to her husband, “try this, try that!” It’s ok.... I’ll find it!

Split the ring, still everything is ok. Can’t find a fault, but there must be one.
Changed the the mcb, just to rule that out.

clamp ammeter on the outgoing legs.... wildly fluctuating between .5, 1, 5, 7A.... keeps jumping up and down.... not a steady rise.

The husband comes home at about 4pm.... he’s an industrial boiler engineer, but hell he needs to stay away from electrics!

“hmm, I’ll have to run an extension into the garage for the freezers.“

“Freezers!?!” As in plural?


Turns out there’s a single socket in the garage, looks like it’s spurred from a double in the kitchen, back to back.
From this socket is an 8! Way extension lead with a fridge freezer, a chest freezer, a tumblr dryer, a couple of battery chargers and.... wait for it.....



a 3kW immersion heater!!

Seriously!


So all these appliances turning on at once is stretching the 13A fuse in the extension lead, but something still has a fault to take out a 32A breaker at random.


I’m going back tomorrow. It’s fixed and working just now. I’ve told him to try each freezer in turn in the socket, but I’ll have to do something else with the immersion, it’s own radial circuit.
 
Before you pop the immersion on its own radial throw it at him he deserves it!...good luck though mate and keep us posted ?
 
I knew it was going to be a struggle as I went round unplugging badly made extension leads upon badly made diy extension leads....
?....as soon as someone rings they other half when you trying work logically round the place and starts giving you advice you know it’s gonna be a ball ache ?....especially if they are an.....”engineer” ?
 
Last edited:
Aha.... now that boiler man has moved the freezer and various other objects from in front of the water tank, I can see what’s going on.
The single socket is actually a double, spurred from another one in the garage.
He was just telling me a load of lies as in where it was supplied from.

The immersion heater on the tank has its own switch and timer, which was behind the fridge... he could have told me that was there.

The plug that was marked “water heater” plugged into the extension lead actually went to some for of pumping equipment for the hot water... unit also hidden by the fridge.
Flex was the same colour and size of what I could see of the immersion... I just couldn’t see the cable route yesterday.


so the increasing amps has been this pump trying to get up and seizing, causing the overload.

I told him to get the pump unit repaired/ replaced, and not overload the extension lead with freezers

3 hours of searching, which could have been found sooner if he’d answered the question “is everything unplugged” correctly.
 
If anyone remembers watching 'House'...... one of his catchphrases was 'The patient always lies'
 

Reply to Strange fault. Time delayed mcb trip. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock