Guys did a consumer unit change over the weekend and hit 2 snags
1. The suppliers cut out fuse has no markings on it ie no BS 88 60 amp instead the unit is black with no markings on it so how to I id it for the cert. The property is a 3 bedroom 1950s flat TNS supply.


2. Maximum demand I have 40A shower 32A cooker 32A ring 32A ring 6A lights 6A lights so what should my figure be ?

thanks in advance
 
It does sound like a BS88, so put that in the box.

To work out your maximum demand add the MCB ratings together and times it by 0.4, and put that figure in the box.

cheers....................Howard
 
Check for the info on the previous certs or inspection reports----:D...sorry oldtimer just being silly

do as SkB advises these details .although necessary,are not too crucial afterall
 
To work out your maximum demand add the MCB ratings together and times it by 0.4, and put that figure in the box.

cheers....................Howard

take the highest rated mcb add up the rest then times them by 0.40 and add the highest breaker to that.


32A cooker 32A ring 32A ring 6A lights 6A lights = 108x0,40 = 43.2

+ 40A shower =
83a
 
Last edited by a moderator:
Just out of interest, would you note, that's the method you used find maximum demand on the cert ?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
suppliers cut out fuse
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
oldtimer,
Last reply from
ezzzekiel,
Replies
5
Views
4,036

Advert